The price of the inverter (UPS) is not the only problem - You also need a bank of deep discharge batteries. These batteries should not be discharged lower than 90% of full capacity if you want the batteries to last long (as an example, if discharged only 10% a battery has a "cycle life" of around 10 000 cycles, but the same battery discharged to 50% will only last about 2000 cycles, if you're lucky.
Thus for a 48V 3KVA inverter supplying full power for 4 hours you will need 3000W/48V=62.5A x 4 hours = 250Ah / 10% = 2500Ah total capacity (without external losses). That would mean 10 x 250Ah 48V batteries, or 40 x 250Ah 12V batteries (if my calculations are correct...), and at (say) R1 000.00 per battery you're talking about R40 000.00.
Any sparkies on the forum to confirm my calculations ?
Hennie