    Hi there I was wondering if someone has some advice on this.....

    I installed a UPS on my system over the weekend to run the 85w return and 3 8w powerheads in case of a power outage

    It is a 1400va UPS so it is supposed to carry the load easily.taking the wattage rating of the UPS will be at about 60% of the VA rating.

    Anyways what happens when I shut all power off is that the bloody UPS kicks in and it seems that the pumps now spin backwards sucking water from display to sump.

    This does not make sense beacuse its AC and polarity should not make a difference.

    Has this anything to do with the sine wave output of the UPS or what can the cause be?????

    Any sugestions as to what to do would be greatly appreciated
     
  2. Guest




  3. Express Reef

    Express Reef

    Joined:
    12 Aug 2011
    Posts:
    2,650
    Likes Received:
    121
    Location:
    Vanderbijlpark
    @Philip.Cloete, When using a ups it must be a pure sinwave or modified sinwave on certain pumps. I know the Atman return pump only work on a pure sinewave where the more exspensive pump like water blaster runs on the modified sinwave @Quintin will be able to tell you more....
     
    Last edited by a moderator: 26 Nov 2015
  4. OP
    Philip.Cloete

    Philip.Cloete

    Joined:
    21 Dec 2010
    Posts:
    332
    Likes Received:
    0
    Location:
    Secunda Mpumalanga
    OK my return pump is tehe reef octopus (bubble blaster i think)

    The ups i am using is mi cpu's UPS so it will be a mod
     
  5. shaunn

    shaunn

    Joined:
    26 Sep 2011
    Posts:
    2,220
    Likes Received:
    36
    Location:
    JHB
    Last edited: 20 Nov 2012
  6. OP
    Philip.Cloete

    Philip.Cloete

    Joined:
    21 Dec 2010
    Posts:
    332
    Likes Received:
    0
    Location:
    Secunda Mpumalanga

    Dont want to buy another one if I can get this one to work dont have alot of power outages but this is just for that one day
     
  7. mariusmeyer

    mariusmeyer

    Joined:
    7 Jul 2009
    Posts:
    3,103
    Likes Received:
    229
    Location:
    Jukskei Park, JHB
    Cant help you on the reverse startup issue.

    You could potentially use the UPS. But you will need to replace the batteries with a deep cycle battery that has a lot more capacity and get an external charger as the charger inside the UPS will not be able to recharge a 100AH battery fast enough. So basically you will only be able to use the UPS as the inverter component.

    If you dont want to change to a deep cycle battery and external charger then you will not get decent backup time. To calculate what you will get out of your current unit you will need to open it up and check the AH ratings of the battery.
     
    Last edited: 20 Nov 2012
  8. OP
    Philip.Cloete

    Philip.Cloete

    Joined:
    21 Dec 2010
    Posts:
    332
    Likes Received:
    0
    Location:
    Secunda Mpumalanga
    The unit has 2 9ah bateries in so I would dwfinetely s2itch to bigger batteries later just trying to get this to run first
     
  9. jacquesb

    jacquesb Retired Moderator

    Joined:
    29 May 2007
    Posts:
    17,868
    Likes Received:
    70
    Location:
    Cape Town
    Philip - I have a ReefOcto 3000 pump for a return pump (65 watt), and mine is connected to a 650VA UPS (for now). This works perfectly well for me. I ONLY have the return pump on the UPS though. I have a PC UPS (probably modified sinewave - not 100% sure).
     
  10. OP
    Philip.Cloete

    Philip.Cloete

    Joined:
    21 Dec 2010
    Posts:
    332
    Likes Received:
    0
    Location:
    Secunda Mpumalanga
    Sorry guys my bad I tested the output voltage when runningon batteries and got 140v at least it was still under guarantee so they swopped it for a 1400va with 3 9ah batterys.......
     

Recent Posts

Loading...
Similar Threads - setup Forum Date
Setup Thread Medium Tanks 14 Jul 2017
[wtd] Zetlight 1201L or similar setup Wanted 13 May 2017
[wtd] Pico or Nano setup [CPT] Wanted 10 Apr 2017
[wtd] Wanted: Small marine setup Wanted 6 Apr 2017
Surgeon's Setup VII Large Tanks 1 Feb 2017
A lot in one thread.... new tank setup at school: General Discussions and Advice 23 Jan 2017
Some advise on planned Marine setup in progress! Beginner Discussions 23 Jan 2017