    hi Guys already have a ups that i would like to use f possible, dont know much on the electrical side so need some help please.

    UPS Specs:
    1000VA / 600 W

    the batteries it has are as per the attached pic which im sure wont last very long, i want to run a 55 watt pump of this UPS.
    will it be able to charge a 12V deep cycle battery

    IMG-20121210-00692.jpg

    IMG-20121210-00693.jpg
     
  2. AdS Guest




    to hide all adverts.
  3. mariusmeyer

    mariusmeyer

    Joined:
    7 Jul 2009
    Posts:
    3,055
    Likes Received:
    210
    Location:
    Jukskei Park, JHB
    The built in charger will not be able to charge a deep cycle battery. It will take a very long time.
     
  4. Wolve

    Wolve Thread Starter

    Joined:
    7 Apr 2009
    Posts:
    310
    Likes Received:
    1
    Location:
    Durbs
    darn i was hoping that might not be the case.

    it has the following batteries "12V/7 Ah x 2pcs" which would be hopeless right.

    so the option would be to use a deep cycle battery with its own charger and use the ups to do the auto change over.
     
  5. Wolve

    Wolve Thread Starter

    Joined:
    7 Apr 2009
    Posts:
    310
    Likes Received:
    1
    Location:
    Durbs
    double post :)
     
    Last edited: 10 Dec 2012
  6. renie

    renie

    Joined:
    22 Apr 2013
    Posts:
    6
    Likes Received:
    0
    Location:
    Alberton
    It also looks like you have your batteries in series. This means you have 2X12volt. 24Volt thus. You will need two 12volt deep cycles also in series. Connected as the ones you have.
     
  7. brettb2020

    brettb2020

    Joined:
    1 Feb 2009
    Posts:
    715
    Likes Received:
    2
    Location:
    Amanzimtoti
    Ive connected a 100AH to a similar UPS and it worked fine. It did take very long to charge though, as Mariusmeyer said.
    Another thing to consider is that UPS probably has a modified sine wave output. Unless its a DC pump it might not run properly or not run all. It may also run one day but the next day it won't. Been there, done that.
     
Recent Posts

Loading...
Similar Threads - Advice Forum Date
Clean up crew advice General Discussions and Advice 19 Nov 2016
Advice on algae growth Nuisance Algae 17 Nov 2016
Advice Needed for Sale of Tank General Discussions and Advice 16 Nov 2016
copepods breeding advice plz General Discussions and Advice 9 Nov 2016
Clownfish fighting - advice please General Discussions and Advice 22 Oct 2016
TL550 Advice Beginner Discussions 3 Oct 2016
Importing an LED unit - Advice needed Technology 12 Sep 2016